消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

当梁高超过600mm,梁间净距1米时,梁间是否设置点式感烟/感温探测器

GB 50116火灾自动报警设计规范有如下要求:

6.2.3 在有梁的顶棚上设置点型感烟火灾探测器、感温火灾探测器时,应符合下列规定:

        3 当梁突出顶棚的高度超过600mm时,被梁隔断的每个梁间区域应至少设置一只探测器。
        5 当梁间净距小于1m时,可不计梁对探测器保护面积的影响。

6.2.5 点型探测器至墙壁、梁边的水平距离,不应小于0.5m。

在实际设计时遇到梁高超过600mm,梁间净距1米,请问梁间是否设置点式感烟/感温探测器?6.2.5条水平距离是否指的是净距离?

Mr.sun | 2025-06-10 15:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

牛丫头消防课堂 2025-06-10 21:33 00 [回复]举报

首先,您说的梁间净距小于 1m与梁突出顶棚的高度超过 600mm同时出现的情况不多见,如果个别区域出现了,那么按照梁突出顶棚的高度超过 600mm处理,需要设置探测器。

6.2.5,就是指探测器边缘至墙壁、梁边的最近的水平距离。

Mr.sun   回复: 牛丫头消防课堂2025-06-11 14:06

首先非常感谢您的答复!发电厂的汽轮机厂房出现了几十处这种情况,结构专业在图纸设计的时候梁间净距正好1米,梁高700-900mm,这些位置还有预作用系统覆盖,按GB 50016须设置火灾自动报警系统,现在几方争执不下最终决定严格卡规范执行,如果6.2.5指的是探测器边缘到墙壁、梁边的净间距,1米净距的梁间设置探测器就违反规范6.2.5的要求(探测器是有大小的),如果不设置又会违反6.2.3的要求。想问一下您回复的6.2.5,就是指探测器边缘至墙壁、梁边的最近的水平距离。”可有出处。

0    0 [回复]举报

牛丫头消防课堂   回复: Mr.sun2025-06-13 10:06

火灾自动报警系统设计规范 GB50116-2013

0    0 [回复]举报

Mr.sun   回复: 牛丫头消防课堂2025-06-16 14:11

您好,6.2.5 点型探测器至墙壁、梁边的水平距离,不应小于0.5m。条文解释:本条规定是参考德国标准和英国规商制定的。探测器至墙 壁、梁边的水平距离,不应小于 0.5m 是为了保证探测器可靠探测。

条文及条文解释中并未明确是探测器的边缘到墙壁、梁边,如果按探测器中心到墙壁、梁边不应小于0.5m,在梁间净距1m的梁间不会造成6.2.3条与6.2.5条条文上的冲突,如果按探测器边缘到墙边、梁边不应小于0.5m,则规范中6.2.3与6.2.5条则会有冲突的情况。

0    0 [回复]举报

李勤 2025-06-12 08:17 00 [回复]举报

Mr.sun   回复: 李勤2025-06-12 11:34

您好,您标注的规范我都理解,梁高600mm以上,梁间净距离整好1米时按6.2.3条要求是要设置探测器的,但6.2.5条又有要求,点型探测器至墙壁、梁边的水平距离,不应小于0.5m,6.2.5条是净距离的话,设置探测器又违反此条要求(探测器是有大小的)。

0    0 [回复]举报

关闭

关闭

手机APP下载