消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

储烟仓范围内的排风口, 距离地面高度 需不低于2米的规范依据在  哪里 ?














有专家提出这问题,却无提供依据。 地下停车场,  消防排烟机的排风口,已经在储烟仓范围内,但风口 距离地面高度 需不低于2米的规范依据在  哪里 ? 依据在哪里(计算公式、 规范、图集都找不到明确依据 )???



























知耻也要问 | 2024-12-13 16:30
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

LHH2737 2024-12-13 16:43 10 [回复]举报

应该是考虑到室内净高

通规第7.1.5 在疏散通道、疏散走道、疏散出口处,不应有任何影响人员疏散的物体,并应在疏散通道、疏散走道、疏散出口的明显位置设置明显的指示标志。疏散通道、疏散走道、疏散出口的净高度均不应小于2.1m。疏散走道在防火分区分隔处应设置疏散门。

潘天坤 2024-12-13 16:54 30 [回复]举报

人员正常活动的场所或者疏散通道的2米或者2.1米位置如果存在风管、风口或者其他障碍物,可能会违反相关规范的净高要求

还有就是除非室内净高比较低或者受现场因素影响,不然一般情况下设计风管或者排烟口高度很少低于2.1米


建筑防火通用规范GB55037、民用建筑设计统一标准GB50352、民用建筑通用规范GB55031里都有提到类似的内容:疏散通道、疏散走道、疏散出口的净高度均不应小于2.1米(建筑防火通用规范GB55037);地下室、局部夹层、公共走道、建筑避难区、架空层等有人员正常活动的场所最低处室内净高不应小于2米(民用建筑通用规范GB55031);地下室、局部夹层、走道等有人员正常活动的最低处净高不应小于2米(民用建筑设计统一标准GB50352)




关闭

关闭

手机APP下载