消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

新规范里边不允许套间了么?

在建筑防火通用规范GB 55037-2022中,第7.1.2条  建筑中的疏散出口应分散布置,房间疏散门应直接通向安全出口,不应经过其他房间。里边规定不能做套间了?是这个意思吗?或者套间的门不属于房间疏散门么?我在设计图纸时,设计院根据这条跟我说不能做套间或者套间不能设置门,所以问问大佬们这个合理吗?或者有什么其他解释?

无敌肉肉 | 2025-02-21 14:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

小唐12321 2025-02-21 14:53 00 [回复]举报

还真没发现,你就说这不属于其他房间,整体是一个房间,里面疏散距离满足也不行吗

LHH2737 2025-02-21 14:58 20 [回复]举报

允许套间,比如说酒店里比较高级的套间会有个客厅,然后再往里才是房间。疏散门指的是房间通向过道的门,里面那个房间通向客厅的门不属于疏散门,不违反这条规范。

唯一要注意的是这种情况下,客厅和房间的面积加起来的总面积才是这个房间的建筑面积,要根据总面积来考虑疏散门和排烟设计。

建筑设计防火规范条文解释5.5.8:由于在实际执行规范时,普遍认为安全出口和疏散门不易分清楚。为此,本规范在不同条文作了区分。疏散门是房间直接通向疏散走道的房门、直接开向疏散楼梯间的门(如住宅的户门)或室外的门,不包括套间内的隔间门或住宅套内的房间门;

LHH2737 2025-02-21 15:09 10 [回复]举报

另外补充一点,这条规范指的是所有建筑,也就是包括住宅建筑在内,住宅没有套间那是不可能的

关闭

关闭

手机APP下载