高大空间自然排烟时,挡烟垂壁高度如何设计

高大空间自然排烟时,挡烟垂壁高度如何设计


例如一大堂连通一层和二层,每层高4米,大堂面积600平方米,未设置防火卷帘。则大堂上下两侧处挡烟垂壁高度如何设计。


又例如:一栋三层内廊建筑,层高3米,内廊中部一区域有一垂直连通的天井(天井面积约50平方米,顶部有屋面板,可开侧窗)。内廊为自然排烟,开井处挡烟垂壁高度如何设计。

消防网友78337 | 2021-05-25 11:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

刘丽波 2021-05-25 16:13 00 [回复]举报

例一,大堂与相邻非大堂部分为不同防烟分区,一层按一层非大堂部分防烟分区的储烟仓高度设置挡烟垂壁;二层按大堂与相邻非大堂部分两个防烟分区的储烟仓的大者考虑挡烟垂壁。

例二,与例一处理方式相同。天井部分面积虽然小于100平,但天井部分所属房间面积大于100平,也需考虑排烟。有个别地方标准有特殊要求除外。

消防网友78337   回复: 刘丽波2021-05-26 07:26

收到谢谢

依思路1.不同高程空间,防烟分区应分别设置

问题二中,2.天井大于100平方,且高度超6米,自然开窗是否难以达到。3.如果天井面积X3小于100平方米,可不考虑排烟吗?

0    1 [回复]举报

刘丽波   回复: 消防网友783372021-05-26 10:52

不同高程空间可以划一个防烟分区,按最高的考虑。这两个不同高程空间应在一个楼层,防烟分区不建议跨楼层。

天井不管多大,平时通风采光都可,火灾排烟时要注意防止火灾蔓延。天井处,不能自然排烟就做机械的。民用建筑术语标准的中庭定义与个别地方标准不一样,没有面积要求。此处有争议,建议按较严规范执行。

1    0 [回复]举报

消防网友67906 2022-04-07 08:42 00 [回复]举报

例二中     天井是和大气相通的   顶部有屋面就不是天井了,应该为中庭。