消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问新风系统(或送风系统或日常排风换风系统或空调系统)管道在每个防烟分区支管处是否需要设置防火阀?

漂移 | 2021-11-02 08:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

@mad 2021-11-03 18:05 00 [回复]举报

个人认为穿防火隔墙、防火墙、接风井这些地方要加防火阀


暖通洲 2022-02-14 15:17 00 [回复]举报

规范对此无要求,穿越防烟分区的水平风管由于热压不会成为烟气大量流窜的通道,故从规范及实际角度看普通通风管道无设置防火阀的必要。

潘天坤 2024-07-01 13:55 00 [回复]举报

非排烟系统就没有防烟分区的概念,是否需要设置防火阀主要取决于穿越墙体是否为防火隔墙,是否为重要区域,常见就是对比此墙体是否有开设防火门,如果有防火门一般会认为是重要区域而设置防火阀

按照建筑防火通用规范 GB55037-2022第6.3.5条规定:通风和空气调节系统的管道、防烟与排烟系统的管道穿过防火墙、防火隔墙、楼板、建筑变形缝处,建筑内未按防火分区独立设置的通风和空气调节系统中的竖向风管与每层水平风管交接的水平管段处均应采取防止火灾通过管道蔓延至其他防火分隔区域的措施
结合条文说明和实施指南来理解,各类风管穿越防火隔墙,应设置防火阀等防火分隔措施并且做好防火保护措施以防止烟气和火势蔓延

王发发   回复: 潘天坤2025-02-13 08:30

那这些防火阀需要装模块接消防主机吗?

0    0 [回复]举报

潘天坤   回复: 王发发2025-02-13 14:46

防烟系统、排烟系统、与防排烟系统合用的通风空调系统、防排烟系统中设于空调通风管道出口的防火阀,这些部位有信号反馈要求,其余一般不需要(区域内有技术文件特别要求的情况除外)

0    0 [回复]举报

潘天坤   回复: 王发发2025-02-13 14:46

防烟系统、排烟系统、与防排烟系统合用的通风空调系统、防排烟系统中设于空调通风管道出口的防火阀,这些部位有信号反馈要求,其余一般不需要(区域内有技术文件特别要求的情况除外)

0    0 [回复]举报

关闭

关闭

手机APP下载