消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配电房风机房等设备房内是否需要安装疏散指示标识?

配电房风机房等设备房内是否需要安装疏散指示标识?依据是什么?

大苏 | 2022-03-09 11:54
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

陈曲 2022-03-09 12:11 00 [回复]举报

建规 10.3 配电房甚至还要备用照明

五棱镜中看世界 2022-03-21 15:58 00 [回复]举报

需要安装应急照明及疏散指示系统中的备用照明,不是疏散指示。

依据建筑设计防火规范10.3.3 消防控制室、消防水泵房、自备发电机房、配电室、防排烟机房以及发生火灾时仍需正常工作的消防设备房应设置备用照明,其作业面的最低照度不应低于正常照明的照度。

潘天坤 2024-07-03 18:33 00 [回复]举报

风机房好像没有要求设置疏散指示标志,发生火灾时仍需工作、值守的配电室需要设置备用照明、疏散照明和疏散指示标志(发生火灾时不需工作、不需要值守的配电室可以不设置)

消防应急照明和疏散指示系统技术标准 GB51309-2018第3.8.1条规定:避难间(层)及配电室、消防控制室、消防水泵房、自备发电机房等发生火灾时仍需工作、值守的区域应同时设置备用照明、疏散照明和疏散指示标志。

关闭

关闭

手机APP下载