高层建筑旁边的景观树木距离有无要求

高层建筑旁边的景观树木距离有无要求,记得之前验收提过此类问题,现在找规范找不到了,大神们可有知道的,望告知

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防网友76443 2022-05-13 09:34 00 [回复]举报

不应影响消防车道的净空高度和净宽。

骑车单车逛街   回复: 消防网友764432022-05-13 15:48

谢谢

0    0 [回复]举报

荔枝 2022-05-13 11:32 00 [回复]举报

在《建筑设计防火规范》  7.1.8 3.消防车道与建筑之间不应设置妨碍消防车操作的树木、架空管线等障碍物;  7.2.2  1.消防车登高操作场地与厂房、仓库、民用建筑之间不应设置妨碍消防车操作的树木、架空管线等障碍物和车库出入口。

骑车单车逛街   回复: 荔枝2022-05-13 15:48

谢谢

0    0 [回复]举报