 GB50084-2017 》7.1.10中的挡水板时为了防止上方喷头喷水时下方喷头被淋,从而影响喷头的爆破效率。条文中提到不应采用挡水板作为喷头爆破的辅助设施。《GB50067-2014》7.2.6中提到喷头布置还应符合下列规定:应设置在汽车库停车位的上方或侧上方,对于机械式汽车库,尚应按停车的载车板分层布置,且应在喷头的上方设置集热板。

实际工作中经常将两者混淆,请问各位老师,集热板和挡水板在外形上有什么区别?集热板究竟有没有实际作用?个人理解认为,汽车库中的集热板其实主要还是用于挡水,是这样吗?

董华 | 2022-08-03 10:34
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

周家斌 2022-08-03 14:16 00 [回复]举报

两个规范的不一致的地方,GB50084后来才改为挡水板的命名。把原来2001版本“集热挡水板”改成“挡水板”;基本功能就是挡水板功能的。

深圳消防 2022-08-04 14:07 10 [回复]举报

从实验来看,集热板无法集热,故后面规范去掉集热一词。