消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教大师们:建筑面积不大于5000平方米的丁类生产车间内无窗房间是否要设排烟设施 :

请教大师们:建筑面积不大于5000平方米的丁类生产车间内无窗房间是否要设排烟设施 :
消防网友21903 | 2020-11-11 17:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

刘丽波 2020-11-11 20:25 00 [回复]举报

执行《建规》8.5.4,地上建筑的无窗房间,当总建筑面积大于200平方米或一个房间建筑面积大于50平方米,且经常有人停留或可燃物较多时,需要设置排烟设施。

潘天坤 2024-06-18 15:49 00 [回复]举报

建筑面积大于50平方米的无可开启外窗的房间,当可燃物较多或者经常有人停留,应设置排烟设施

单个丁类生产车间(除高温生产工艺的丁类厂房外)建筑面积大于5000平方米,应设置排烟设施

李勤 2025-06-04 15:30 00 [回复]举报


关闭

关闭

手机APP下载