消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

双电源切换箱

6 消防末端配电箱应设置在消防水泵房、消防电梯机房、消防控制室和各防火分区的配电小间内;各防火分区内的防排烟风机、消防排水泵、防火卷帘等可分别由配电小间内的双电源切换箱放射式、树干式供电。



设计防火10.1.8 消防控制室、消防水泵房、防烟和排烟风机房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱处设置自动切换装置。


问下老师,这个双电源配电箱是按哪条规范为主,需不需要每个风机房均设双电源切换箱。

消防网友73525 | 2023-05-23 16:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

安洪全 2023-05-23 16:19 00 [回复]举报

需要

您的问题中就有您要的答案


消防网友73525   回复: 安洪全2023-05-23 16:29

你好老师,我问的是每个风机房,各防火分区我看到了,还有这个双电源是按哪个规范为主。

0    0 [回复]举报

安洪全   回复: 消防网友735252023-05-23 17:07

建筑防火通用规范 GB55037-2022

10.1.6 除按照三级负荷供电的消防用电设备外,消防控制室、消防水泵房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱内设置自动切换装置。

防烟和排烟风机房的消防用电设备的供电,应在其配电线路的最末一级配电箱内或所在防火分区的配电箱内设置自动切换装置。

防火卷帘、电动排烟窗、消防潜污泵、消防应急照明和疏散指示标志等的供电,应在所在防火分区的配电箱内设置自动切换装置。

1    0 [回复]举报

消防网友73525 2023-05-23 16:27 00 [回复]举报

你好老师我问的是每个风机房,不是每个防火分区。

安洪全   回复: 消防网友735252023-05-23 17:12

建筑防火通用规范 GB55037-2022

10.1.6防烟和排烟风机房的消防用电设备的供电,应在其配电线路的最末一级配电箱内或所在防火分区的配电箱内设置自动切换装置。

如果一个防火分区内只有一个配电箱,就在这一个做自动切换,有多个时,在其配电线路的最末端做自动切换。


条文说明:本条规定了建筑中消防用电设备配电的基本要求,以避免配电干线故障影响消防用电设备的供电可靠性。     本条规定的最末一级配电箱,对于消防控制室、消防水泵房的消防用电设备及消防电梯等,为上述消防电梯和消防设备室处的最末级配电箱;对于其他消防用电设备,为这些用电设备所在防火分区的配电箱。


还有,老师不敢当,共同学习,共同进步。

1    0 [回复]举报

一直在路上_WlpS   回复: 安洪全2024-10-11 09:24

10.1.6 本条规定了建筑中消防用电设备配电的基本要求,以避免配电干线故障影响消防用电设备的供电可靠性。     本条规定的最末一级配电箱,对于消防控制室、消防水泵房的消防用电设备及消防电梯等,为上述消防电梯和消防设备室处的最末级配电箱;对于其他消防用电设备,为这些用电设备所在防火分区的配电箱。

0    0 [回复]举报

关闭

关闭

手机APP下载