消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

普通电梯防烟要求

普通电梯防烟要求

羊仔 | 2023-05-25 19:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-05-26 08:56 00 [回复]举报

普通电梯没有防烟要求的,但是对耐火性有要求


电梯制造与安装安全规范 第1部分:乘客电梯和载货电梯 GB/T7588.1-2020 

5.3.5.2 火灾情况下的性能     层门应符合建筑物火灾保护有关法规的规定,这些层门应按GB/T 24480(没找到这本规范)或GB/T 27903的要求进行试验。


电梯层门耐火试验 完整性、隔热性和热通量测定法 GB/T27903-2011

8.2 耐火性能判定 8.2.1 完整性(E) 按GB/T 9978.1的规定进行测量,当发生以下情况之一时,则试件失去完整性,

a) 棉垫被点燃(非隔热型电梯层门除外);

b) 试件背火面出现持续火焰达10s以上;

c) 直径6mm±0.1mm探棒穿过缝隙进入炉内,并沿缝隙长度方向移动不小于150mm;

d) 直径25mm±0.2mm探棒穿过缝隙进入炉内。

8.2.2 隔热性(I) 按GB/T 7633的规定进行测量,当发生以下情况之一时,则试件失去隔热性:

a) 试件背火面平均温升超过140℃(门框上的测温热电偶除外),如门扇由不同的隔热区域构成, 则不同的隔热区域的平均温升应分别计算;

b) 试件背火面单点最高温升超过180℃ (门框上的测温热电偶除外);

c) 试件背火面门框单点最高温升超过360℃。

8.2.3 热通量(W) 试件背火面热通量超过临界热通量值15kW/㎡。

安洪全   回复: 安洪全2023-05-26 14:48

建筑设计防火规范 GB50016-2014(2018年版)

6.2.9  建筑内的电梯井等竖井应符合下列规定:     

1 电梯井应独立设置,井内严禁敷设可燃气体和甲、乙、丙类液体管道,不应敷设与电梯无关的电缆、电线等。电梯井的井壁除设置电梯门、安全逃生门和通气孔洞外,不应设置其他开口。     

2 电缆井、管道井、排烟道、排气道、垃圾道等竖向井道,应分别独立设置。井壁的耐火极限不应低于1.00h,井壁上的检查门应采用丙级防火门。     

3 建筑内的电缆井、管道井应在每层楼板处采用不低于楼板耐火极限的不燃材料或防火封堵材料封堵。     建筑内的电缆井、管道井与房间、走道等相连通的孔隙应采用防火封堵材料封堵。    

4 建筑内的垃圾道宜靠外墙设置,垃圾道的排气口应直接开向室外,垃圾斗应采用不燃材料制作,并应能自行关闭;    

5 电梯层门的耐火极限不应低于1.00h,并应符合现行国家标准《电梯层门耐火试验  完整性、隔热性和热通量测定法》GB/T 27903规定的完整性和隔热性要求。

0    0 [回复]举报

hnlyplszq 2023-05-26 09:44 00 [回复]举报

电梯井道贯各个楼层,普通电梯与消防电梯的层门一样,均需满足耐火完整性和烟密闭性的要求。

关闭

关闭

手机APP下载