消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问走道排烟两端设有不低于2平方米的自然排烟窗,中间区域的防烟分区是否还需要增设排烟设施?

如图所示,公共建筑中一条走道两端设有不低于2平方米的自然排烟窗,但因为走道宽度大于2.5m,无法将防烟分区长度规划到60m,并因为走道净高3m,从而划分为3个防烟分区,根据《烟规》第4.6.3-3条规定,在走道两端设有不低于2平方米的自然排烟窗,现存在一个问题:因为利用挡烟垂壁划分了3个防烟分区,导致防烟分区二存在烟无处可排,是否还需要对防烟分区二进行额外增设排烟设施?


澜沐 | 2023-09-12 15:23
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

陈曲 2023-09-13 11:09 10 [回复]举报

规范原文是 公共建筑、工业建筑中的走道宽度不大于2.5m时,其防烟分区的长边长度不应大于60m

你现在不能到60的原因应该是任一点到排烟窗距离不应大于30 

不低于2平米的窗不代表可开启面积不低于2平米 更不代表有效排烟面积不小于2平米 

所以如果走廊小于60米 可以考虑三个防烟分区是否多余 

澜沐   回复: 陈曲2023-09-13 15:11

我把数据具象化一点,疏散走道长度约51m,走道宽度>2.5m,因为走道宽度>2.5m故不能采用"公共建筑、工业建筑中的走道宽度不大于2.5m时,其防烟分区的长边长度不应大于60m"这一条,只能依照空间净高3m去设置一个防烟分区(即长边最大24m),划分之后还有余下长度从而划分到第三个防烟分区,那么这个夹在中间的防烟分区是否还要增设排烟设施呢?

0    0 [回复]举报

明月夜   回复: 澜沐2023-09-13 16:13

建筑设计防火规范GB50016-2014(2018年版)8.5.3第5条建筑内长度大于20m的疏散走道应设置排烟设施。疏散走道的长度不会因为你分隔防烟分区而变短。你中间分出多少个防烟分区都是要考虑设置排烟设施。

0    0 [回复]举报

陈曲   回复: 澜沐2023-09-21 12:42

这一条是不是可以这么理解 大于2.5时 可以超过60米

0    0 [回复]举报

whale 2023-09-13 17:16 00 [回复]举报

每个防烟分区都要考虑排烟,你这个划分成三个防烟分区则每个防烟分区都应按照建筑防烟排烟系统技术标准4.6.3第三条或者第四条设置排烟设施。

关于走道防烟分区划分需要参考各个地方的解释,下图是截自《浙江省消防技术规范难点问题操作技术指南2020年版》可以参考。

设计中也有些地区要求走道若局部大于2.5m,只要长度小于60m且走道面积不大于150平也可划为一个防烟分区。

潘天坤 2024-06-20 00:42 00 [回复]举报

防烟分区2需要设置排烟设施,不具备自然排烟条件应设置机械排烟。

然后楼主确定其他两个防烟分区的排烟设施符合规范要求?

关闭

关闭

手机APP下载