我想咨询一个关于消防设施设置的问题:
有一栋高层建筑前期建设时已设置了消防设施。
现在有一个用防火墙重新隔了个店面,但按规范可以不用设消防设施。
请问像这种情况分隔出来的店面要不要设消防设施呢?

陈工陈 | 2024-01-02 09:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

阳明心 2024-01-02 09:51 00 [回复]举报

请问“按规范可以不用设消防设施”具体是指哪个规范条款呢?

柳儿 2024-01-02 11:24 10 [回复]举报

需要,消防设施是按总建筑规模来定的,不是按防火分区。

GANSTER 2024-01-03 09:17 00 [回复]举报

既有建筑改造,不管报不报审,请找家正规的专业设计单位

2024-01-03 11:09 00 [回复]举报

假设把该建筑用防火墙重新隔出若干个店面,那能不能都不用设各类消防设施呢?


无论怎样分隔,也是高层建筑的一部分,需要设的设施一样也不能少。


马先生 2024-03-14 15:18 00 [回复]举报

同一栋高层建筑内;无论分隔多少个不同使用功能的场所,消防设施都按整栋建筑计算。