消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

老工程项目,电气火灾一直报警,剩余电流超出报警值,如何处理?改造可以用什么方案?

各位大佬,问题如题。是否做过相同的改造案例,欢迎指教。

个人不成熟的想法:一、将剩余电流探测器安装在下一级配电箱;二将原来的剩余电流探测器换成测温式探测器。

蓝泰 | 2024-01-13 22:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2024-01-15 10:24 00 [回复]举报

火灾自动报警系统设计规范 GB50116-2013

9.2.1 剩余电流式电气火灾监控探测器应以设置在低压配电系统首端为基本原则,宜设置在第一级配电柜(箱)的出线端。在供电线路泄漏电流大于 500mA 时,宜在其下一级配电柜(箱)设置。

9.2.2 剩余电流式电气火灾监控探测器不宜设置在 IT 系统的配电线路和消防配电线路中。

9.2.3 选择剩余电流式电气火灾监控探测器时,应计及供电系统自然漏流的影响,并应选择参数合适的探测器;探测器报警值宜为 300mA~500mA 。 9.2.4 具有探测线路故障电弧功能的电气火灾监控探测器,其保护线路的长度不宜大于 100m 。

蓝泰   回复: 安洪全2024-01-20 09:27

谢谢,但是无法解决现实问题:一是因为老项目,线路改变较多,末级配电箱很有可能自然漏流量也大于报警值,同时检查线路比较困难。二是重新放线增加探测点位成本较高。提问的意思是比较两种方案的优劣,第二种方案在实际中是否有应用案例?

0    0 [回复]举报

马先生 2024-03-14 15:03 00 [回复]举报

电气火灾设备;在一般老旧场所设置,如果经常出现报警,说明线路存在问题,要想彻底解决,需要重新敷设线路。但是实际情况难以投入改造;可以把探测剩余电流器取消,换成探测温度器(电线发热报警)。

关闭

关闭

手机APP下载