消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

有效容积该如何确定

《消防给水及消火栓系统技术规范》4.3.4  当消防水池采用两路消防供水且在火灾情况下连续补水能满足消防要求时,消防水池的有效容积应根据计算确定,但不应小于100m3,当仅设有消火栓系统时不应小于50m3。这里的50、100的要求是只针对消防水池采用两路消防供水且在火灾情况下连续补水能满足消防要求这种情况下的吗。如果是一路消防供水也是不应小于100m3,当仅设有消火栓系统时不应小于50m3吗。

消防网友23971 | 2021-02-02 11:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

刘丽波 2021-02-02 12:16 00 [回复]举报

此处规范并不明确。如实际计算中不考虑补水,火灾延续时间内全部水量比50或100立方米小,可以取实际计算值。可以参考给排水问题集锦96-98题。

消防网友23971   回复: 刘丽波2021-02-02 15:12

感谢解答!

0    0 [回复]举报

消防网友73154 2021-02-03 10:20 00 [回复]举报

只有两路供水才能保证供水的可靠性,所以50和10只是针对两路供水的

李勤 2021-03-19 14:00 00 [回复]举报

正常水池按灭火设施用水量就算。如果双路供水,按最小供水数值减少,但不能小于上述50、100.

关闭

关闭

手机APP下载