消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

办公楼喷淋设置问题

请教多层办公楼,总面积大于3000,仅局部设置集中空调面积1000平,是仅在设置集中空调所在的防火分区设置喷淋,还是因为设置集中空调的面积没超过3000可不设置,如果设置的话,是只要总面积超3000,局部做集中空调的话,不管面积多大,都要在所在防火分区设置喷淋吗

深渊下的魔 | 2024-06-14 06:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

shawu 2024-06-14 14:15 00 [回复]举报

设置集中空调的面积没超过3000可不设置

潘天坤 2024-06-15 12:05 00 [回复]举报

建规和防火通规正文的描述,形成了很多理解。

一些地区的技术文件认为:设置集中的场所面积要超过3000平方米才需要设置,可以只设置在有设置集中的场所。

还有需要注意的是,建规和防火通规的描述有一定的区别,例如:防火通规描述的是“除外”,执行起来也有一定的区别。

个人建议:查阅区域内技术文件要求,再跟区域内设计、审查、验收专家们交流,看看主流思想是怎么样的。

关闭

关闭

手机APP下载