关于建筑防火通用规规范 55037-2022中第8.2.5条先相关疑问。

建筑防火通用规规范 55037-2022中第8.2.5条 

建筑中下列经常有人停留或可燃物较多且无可开启外窗的房间或区域应设置排烟设施:

1 建筑面积大于50㎡的房间;

2 房间的建筑面积不大于50㎡,总建筑面积大于200㎡的区域。


综上,按照第2条的说法及之前网友解答的意思是:

这段话为网友解答:(小于等于50m²的无外窗房间,这类房间的建筑面积相加只要不大于200m²,可以通过走道排烟,也就是说走道需要设置排烟设施)。

1.那么一个场所如果无窗房间加起来不大于200m²,需要通过走道对这些不大于50m²的房间进行排烟时是否需要把过道的面积一起算进去?

2.如果一个场所不大于50m²的无窗房间加起来大于了200m², 又该如何处理?是应该继续通过过道排烟吗?


Jack—001 | 2024-08-12 15:56
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

GANSTER 2024-08-14 11:36 00 [回复]举报

区别就在于是否有走道及走道的长度:情况1,当无走道或有走道但长度不大于20米时,走道及房间不用考虑排烟;当有走道且走道长度超过20米时,仅在走道设排烟,方式可自然可机械。情况2,有走道则无论走道是否大于20米,都宜在走道设置排烟且为机械方式;若无走道则应在每个房间设置排烟,可自然可机械。

Jack—001   回复: GANSTER2024-08-20 10:43

谢谢!

0    0 [回复]举报

潘天坤 2024-09-12 15:25 10 [回复]举报

建筑GB50016的配套图集关于无窗房间200平方米的定义与建筑防火通用规范GB55037配套实施指南有一定的出入(主要在于是否要计入房间外走道等公共区域的面积),从时效性和规范地位来说,目前应按建筑防火通用规范GB55037配套实施指南执行

1、每个无可开启外窗房间不大于50平方米(包括50),无可开启外窗房间区域的总建筑面积(不包括房间外走道等公共区域的建筑面积)不大于200平方米(包括200),走道及房间均不需要设置排烟设施

2、每个无可开启外窗房间不大于50平方米(包括50)时,无可开启外窗房间区域的总建筑面积(不包括房间外走道等公共区域的建筑面积)大于200平方米时,每个房间可不设置排烟设施,可以在走道设置排烟设施,与走道连接的房间可以通过走道排烟

3、歌舞娱乐放映游艺场所的情况可能需要再分析